help fault finding a tripped fuse

Post by Mr Red »

Overnight a fuse in the consumer box of my house tripped. The fuse is for the sockets in 3 rooms. If I turn the fuse on then the RCD trips. I unplugged everything from all the sockets but still when I turn the fuse on the RCD trips. What is the next step in fault finding?
Neelix
Senior Member
Posts: 1368
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 219 times

help fault finding a tripped fuse

Post by Neelix »

Call somebody competent with proper test kit?
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

help fault finding a tripped fuse

Post by aeromech3 »

:withstupid: serious problem, just my 2 penny worth: assuming Mrs Red has not been hanging pictures up on the wall with hammer and nail overnight what high load items did you have on that circuit ? you could well have a cable (ring or spur) overheated with insulation melted and there is now a track to the earth wire.
User avatar
Someone-Else
Senior Member
Posts: 14848
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 48 times
Been thanked: 2606 times

help fault finding a tripped fuse

Post by Someone-Else »

Although this is a DIY forum, there are some jobs that are either not really DIY or above the capabilities of the poster, particularly where electricity is concerned a lot of people assume "Well it works, so it must be OK"
I have to say that abrupt that the answer is, what Neelix said is the next step, unless you have an MFT and know how to use it, but if you did have one, you would not be asking here, so call an electrician it is then.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
OnlineOnline
User avatar
Mr Red
Newly registered Member
Posts: 94
Joined: Mon Feb 26, 2007 9:13 pm
Has thanked: 50 times
Been thanked: 0

help fault finding a tripped fuse

Post by Mr Red »

aeromech3 wrote: Sun Jan 15, 2023 2:55 pm :withstupid: serious problem, just my 2 penny worth: assuming Mrs Red has not been hanging pictures up on the wall with hammer and nail overnight what high load items did you have on that circuit ? you could well have a cable (ring or spur) overheated with insulation melted and there is now a track to the earth wire.
It was in the middle of the night so I can't blame Mrs Red unfortunately. The only load of any note was the gas combi boiler but that only has a 3A fuse. My initial thought was that perhaps a mouse had chewed through a cable somewhere. So I figured that testing with an insulation tester might be in order. I've always wanted one so maybe now's the time to buy although I'm not sure where to stick it so to speak. (I'm an electronics engineer, so not a complete dullard in the ways of the electron. I'm not familiar with the circuitry of a house though)
Neelix
Senior Member
Posts: 1368
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 219 times

help fault finding a tripped fuse

Post by Neelix »

My money is on a boiler problem.

Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
These users thanked the author Neelix for the post:
aeromech3 (Sun Jan 15, 2023 4:30 pm)
Rating: 7.14%
User avatar
aeromech3
Senior Member
Posts: 3598
Joined: Fri Feb 26, 2010 11:16 am
Location: Ash Surrey
Has thanked: 177 times
Been thanked: 665 times

help fault finding a tripped fuse

Post by aeromech3 »

Though I agree with all the above and not a dullard too, I would isolate all the electrical supply at the C.U. yes master off as you don't know for sure that another circuit is involved, and go around each of the wall sockets, starting with the most used on fault side, and check the back connections, I don't think this is outside the realms of a DIY'r.
I have had houses where due use or vibration, a clamping screw has loosened and the wire potentially could have made contact with the earthed metal back box.
User avatar
Mr Red
Newly registered Member
Posts: 94
Joined: Mon Feb 26, 2007 9:13 pm
Has thanked: 50 times
Been thanked: 0

help fault finding a tripped fuse

Post by Mr Red »

Neelix wrote: Sun Jan 15, 2023 4:20 pm My money is on a boiler problem.

Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
yes, I isolated the boiler by removing its fuse. Will have to do some research on fused spurs - it means nothing to me!
User avatar
Mr Red
Newly registered Member
Posts: 94
Joined: Mon Feb 26, 2007 9:13 pm
Has thanked: 50 times
Been thanked: 0

help fault finding a tripped fuse

Post by Mr Red »

aeromech3 wrote: Sun Jan 15, 2023 4:29 pm Though I agree with all the above and not a dullard too, I would isolate all the electrical supply at the C.U. yes master off as you don't know for sure that another circuit is involved, and go around each of the wall sockets, starting with the most used on fault side, and check the back connections, I don't think this is outside the realms of a DIY'r.
I have had houses where due use or vibration, a clamping screw has loosened and the wire potentially could have made contact with the earthed metal back box.
I could certainly do that.
Neelix
Senior Member
Posts: 1368
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 219 times

help fault finding a tripped fuse

Post by Neelix »

Mr Red wrote: Sun Jan 15, 2023 4:56 pm
Neelix wrote: Sun Jan 15, 2023 4:20 pm My money is on a boiler problem.

Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
yes, I isolated the boiler by removing its fuse. Will have to do some research on fused spurs - it means nothing to me!
It this confuses you then get somebody in
Grumps
Senior Member
Posts: 1037
Joined: Wed Jun 13, 2007 7:47 pm
Location: Worcestershire/Warwickshire/Gloucestershire (ish)
Has thanked: 51 times
Been thanked: 152 times

help fault finding a tripped fuse

Post by Grumps »

I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.

I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.

Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.

Damn. That could have been somewhat lethal! :cb
Neelix
Senior Member
Posts: 1368
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 118 times
Been thanked: 219 times

help fault finding a tripped fuse

Post by Neelix »

Grumps wrote: Sun Jan 15, 2023 8:51 pm I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.

I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.

Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.

Damn. That could have been somewhat lethal! :cb
That single product should not have 2 points of isolation …
User avatar
Mr Red
Newly registered Member
Posts: 94
Joined: Mon Feb 26, 2007 9:13 pm
Has thanked: 50 times
Been thanked: 0

help fault finding a tripped fuse

Post by Mr Red »

Grumps wrote: Sun Jan 15, 2023 8:51 pm I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.

I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.

Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.

Damn. That could have been somewhat lethal! :cb
I have a similar situation - the extractor hood and lights have their own socket which I'd forgotten all about when unplugging everything else as it's hidden away at the back of a cupboard. I unplugged it but that's not the problem.
User avatar
Mr Red
Newly registered Member
Posts: 94
Joined: Mon Feb 26, 2007 9:13 pm
Has thanked: 50 times
Been thanked: 0

help fault finding a tripped fuse

Post by Mr Red »

Neelix wrote: Sun Jan 15, 2023 6:46 pm
Mr Red wrote: Sun Jan 15, 2023 4:56 pm
Neelix wrote: Sun Jan 15, 2023 4:20 pm My money is on a boiler problem.

Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
yes, I isolated the boiler by removing its fuse. Will have to do some research on fused spurs - it means nothing to me!
It this confuses you then get somebody in
I've done some reading. Unfortunately I'm not at home to check what type of FCU I have. What do you think could be happening if the FCU is single pole?
User avatar
Someone-Else
Senior Member
Posts: 14848
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 48 times
Been thanked: 2606 times

help fault finding a tripped fuse

Post by Someone-Else »

Mr Red wrote: Mon Jan 16, 2023 1:17 pm What do you think could be happening if the FCU is single pole
You will need to do some more reading (Sorry, but you did ask) You have not (yet) grasped the "complexity" of the problem and why single pole is not ideal.

If the answer/reason was given to you on a plate, you would not learn.
Above are my opinions Below is my signature.