help fault finding a tripped fuse
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
Overnight a fuse in the consumer box of my house tripped. The fuse is for the sockets in 3 rooms. If I turn the fuse on then the RCD trips. I unplugged everything from all the sockets but still when I turn the fuse on the RCD trips. What is the next step in fault finding?
Mr Red
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
Neelix
- aeromech3
- Senior Member
- Posts: 3598
- Joined: Fri Feb 26, 2010 11:16 am
- Location: Ash Surrey
- Has thanked: 177 times
- Been thanked: 665 times
help fault finding a tripped fuse

aeromech3
- Someone-Else
- Senior Member
- Posts: 14848
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2606 times
help fault finding a tripped fuse
Post by Someone-Else »
Although this is a DIY forum, there are some jobs that are either not really DIY or above the capabilities of the poster, particularly where electricity is concerned a lot of people assume "Well it works, so it must be OK"
I have to say that abrupt that the answer is, what Neelix said is the next step, unless you have an MFT and know how to use it, but if you did have one, you would not be asking here, so call an electrician it is then.
I have to say that abrupt that the answer is, what Neelix said is the next step, unless you have an MFT and know how to use it, but if you did have one, you would not be asking here, so call an electrician it is then.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
It was in the middle of the night so I can't blame Mrs Red unfortunately. The only load of any note was the gas combi boiler but that only has a 3A fuse. My initial thought was that perhaps a mouse had chewed through a cable somewhere. So I figured that testing with an insulation tester might be in order. I've always wanted one so maybe now's the time to buy although I'm not sure where to stick it so to speak. (I'm an electronics engineer, so not a complete dullard in the ways of the electron. I'm not familiar with the circuitry of a house though)aeromech3 wrote: ↑Sun Jan 15, 2023 2:55 pmserious problem, just my 2 penny worth: assuming Mrs Red has not been hanging pictures up on the wall with hammer and nail overnight what high load items did you have on that circuit ? you could well have a cable (ring or spur) overheated with insulation melted and there is now a track to the earth wire.
Mr Red
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
help fault finding a tripped fuse
My money is on a boiler problem.
Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
Did you isolate the boiler? And beware lots of fused spurs are single pole so that type won’t isolate the neutral and the live
Neelix
- aeromech3
- Senior Member
- Posts: 3598
- Joined: Fri Feb 26, 2010 11:16 am
- Location: Ash Surrey
- Has thanked: 177 times
- Been thanked: 665 times
help fault finding a tripped fuse
Though I agree with all the above and not a dullard too, I would isolate all the electrical supply at the C.U. yes master off as you don't know for sure that another circuit is involved, and go around each of the wall sockets, starting with the most used on fault side, and check the back connections, I don't think this is outside the realms of a DIY'r.
I have had houses where due use or vibration, a clamping screw has loosened and the wire potentially could have made contact with the earthed metal back box.
I have had houses where due use or vibration, a clamping screw has loosened and the wire potentially could have made contact with the earthed metal back box.
aeromech3
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
yes, I isolated the boiler by removing its fuse. Will have to do some research on fused spurs - it means nothing to me!
Mr Red
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
I could certainly do that.aeromech3 wrote: ↑Sun Jan 15, 2023 4:29 pm Though I agree with all the above and not a dullard too, I would isolate all the electrical supply at the C.U. yes master off as you don't know for sure that another circuit is involved, and go around each of the wall sockets, starting with the most used on fault side, and check the back connections, I don't think this is outside the realms of a DIY'r.
I have had houses where due use or vibration, a clamping screw has loosened and the wire potentially could have made contact with the earthed metal back box.
Mr Red
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
help fault finding a tripped fuse
It this confuses you then get somebody in
Neelix
-
- Senior Member
- Posts: 1037
- Joined: Wed Jun 13, 2007 7:47 pm
- Location: Worcestershire/Warwickshire/Gloucestershire (ish)
- Has thanked: 51 times
- Been thanked: 152 times
help fault finding a tripped fuse
I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.
I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.
Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.
Damn. That could have been somewhat lethal!
I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.
Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.
Damn. That could have been somewhat lethal!

Grumps
-
- Senior Member
- Posts: 1368
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
help fault finding a tripped fuse
That single product should not have 2 points of isolation …Grumps wrote: ↑Sun Jan 15, 2023 8:51 pm I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.
I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.
Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.
Damn. That could have been somewhat lethal!![]()
Neelix
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
I have a similar situation - the extractor hood and lights have their own socket which I'd forgotten all about when unplugging everything else as it's hidden away at the back of a cupboard. I unplugged it but that's not the problem.Grumps wrote: ↑Sun Jan 15, 2023 8:51 pm I had a similar problem and, although we rarely use it, it turned out to be the cooker hood/extractor.
I'd been meaning to take it down and check for obvious defects until, one day, SWMBO switched on the overhead light of the cooker hood/extractor, even though it was isolated at the fused spur.
Seemingly, the motor/extraction part is controlled by the fused spur but the illumiation portion is on a lighting circuit.
Damn. That could have been somewhat lethal!![]()
Mr Red
- Mr Red
- Newly registered Member
- Posts: 94
- Joined: Mon Feb 26, 2007 9:13 pm
- Has thanked: 50 times
- Been thanked: 0
help fault finding a tripped fuse
I've done some reading. Unfortunately I'm not at home to check what type of FCU I have. What do you think could be happening if the FCU is single pole?
Mr Red
- Someone-Else
- Senior Member
- Posts: 14848
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2606 times
help fault finding a tripped fuse
Post by Someone-Else »
You will need to do some more reading (Sorry, but you did ask) You have not (yet) grasped the "complexity" of the problem and why single pole is not ideal.
If the answer/reason was given to you on a plate, you would not learn.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE