- It is currently Tue Apr 08, 2025 4:06 pm
Installing an external socket
- Has thanked: 39 times
- Been thanked: 3 times
Post by glassescase »
I have an external IP66 double socket with a built in RCD.
If the cable is coming down the wall, looping under the socket and then up in to the socket, does it need to be armoured?
The socket will be about 3 or 4 foot off the ground and from the roof it is about 4 or 5 ft
thanks glassescase
thanks glassescase
glassescase
- Has thanked: 118 times
- Been thanked: 219 times
The circuit requires RCD protection not the socket.
And from your description the cable doesn’t need to be SWA
Neelix
thank you for the advice. I can fit an RCD into the fuse box no problem.
glassescase
glassescase
- ericmark
- Been thanked: 785 times
If cable is buried, so you can't see the cable route in a wall it needs RCD protection, unless using one of the list of which SWA is on the list, but if the cable is not buried then you can still use a RCD socket, or is SWA can be RCD socket. I have two RCD sockets on my UPS supply to the freezers, the all RCBO consumer unit will not protect 5 of my outlets, 4 sockets (2 x doubles) and a FCU to the central heating, so central heating is not RCD protected and I have RCD sockets type A. Type AC no longer permitted, and I tried to get a type A RCD FCU and found I could not get one. At least in CEF.
The cable does not need to be SWA, you can use other cables, for outside normally black as black plastic will resist UV better than white.
ericmark
I don't fully understand your post but I am guessing there is a list of suitable cables for the outside socket. The cable will be on the outside of the wall so visible. Can anyone help with a link to acceptable cable please?ericmark wrote: ↑Tue Oct 31, 2023 12:22 pm If cable is buried, so you can't see the cable route in a wall it needs RCD protection, unless using one of the list of which SWA is on the list, but if the cable is not buried then you can still use a RCD socket, or is SWA can be RCD socket. I have two RCD sockets on my UPS supply to the freezers, the all RCBO consumer unit will not protect 5 of my outlets, 4 sockets (2 x doubles) and a FCU to the central heating, so central heating is not RCD protected and I have RCD sockets type A. Type AC no longer permitted, and I tried to get a type A RCD FCU and found I could not get one. At least in CEF.
This I found https://www.cef.co.uk/catalogue/product ... lsrc=aw.ds
This I did not understand "......or is SWA can be RCD socket", could you please explain?
glassescase
glassescase
You are adding to a circuit so the entire circuit requires RCD protection, so using a RCD socket isn't an option and to be honest is an unnecessary commentglassescase wrote: ↑Tue Oct 31, 2023 12:30 pm >https://www.cef.co.uk/catalogue/product ... w.ds</span>
glassescase
The cable from CEF is ideal for the installation as long as its not going under ground OR would be in a position where it could easily be damaged
- These users thanked the author Neelix for the post:
- glassescase (Tue Oct 31, 2023 1:13 pm)
Neelix
- Approved Electrician
- Has thanked: 225 times
- Been thanked: 664 times
Would the RCD FCU need to be type A unless you are powering something that might give a DC pulse?
OnlyMe
I don't believe you have to install RCD protection for the entire circuit with a small add on.
OnlyMe
If the external socket is a spur and has an inbuilt RCD, why does the whole cct need an RCD? Is it because it is external?
I have seen what looks like cables with plugs fitted and the cable then goes to the external socket. Bit of a risk selling a cable with a plug at one end and nothing at the other.
glassescase
glassescase
glassescase
- ericmark
If that is the case then I need to call NAPIT and complain as I have an installation certificate and compliance certificate issued about 8 weeks ago where the FCU is not RCD protected and the sockets are type A RCD type, cables are not buried in the wall, they are in T2 trunking.
The inverter which supplies them says in the installation manual it needs type AC, they supply three freezers one direct on line, the other two inverter drives.
My copy of BS7671 dates back to 2008, so rules may have changed, but I would not have thought the people who installed my solar panels would have done something non compliant when they knew I was an electrical engineer.
ericmark