Someone-Else wrote: ↑Mon Jun 06, 2022 12:57 pm
Flex is not meant to be used for fixed wiring
Why? I would agree flex costs more than twin and earth, and the current rating is for it being air cooled, so a flex rated at 13 amp when used in a wall may have a lower current rating, and there is a problem with strands getting into screws so a poor termination unless ferrules are used, but in the main flex can be used instead of twin and earth, but twin and earth can't be used instead of flex, wiring a mobile home would always use flex, as the building can flex.
1 mm² twin and earth does not have a single rating, depending on
installation method 1 mm² twin and earth can be 8 to 16 amp depending on installation reference method.
If you look at
table 4F3 click on this link it does say 1 mm² is 10 amp, but then as you continue down it gives de-rating factors, and what you would need to work out is what temperature it will get to when concealed in something which does not allow free air passage, so under a carpet it needs de-rating, it is easier to use the twin and earth tables and installation methods for flex than to work it all out.
But there is nothing to stop flex being used instead of twin and earth other than the price, and use of ferrules if the terminals require it.