What consumer unit?
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
-
- Senior Member
- Posts: 198
- Joined: Fri Jul 01, 2016 7:30 am
- Has thanked: 12 times
- Been thanked: 5 times
What consumer unit?
I will be taking down an internal wall and am needing to relocate the consumer unit. The existing unit is ancient with lots of other boxes spliced off it, so will be upgrading the consumer unit so that I have all the capacity I need in one unit.
I have a friend who is a retired electrician who is willing to help me do the job for free, but he has been retired for about 12 years and is not up on the newer stuff / current best kit. I am looking for something with plenty of capacity as I have plans to do an extension at a later date. I am likely to have up to 4 electric showers and will probably get solar panels and an electric car some time in the future. I think I would rather go for something that is overkill with more capacity than I am likely to need.
Can anyone suggest anything suitable?
I have a friend who is a retired electrician who is willing to help me do the job for free, but he has been retired for about 12 years and is not up on the newer stuff / current best kit. I am looking for something with plenty of capacity as I have plans to do an extension at a later date. I am likely to have up to 4 electric showers and will probably get solar panels and an electric car some time in the future. I think I would rather go for something that is overkill with more capacity than I am likely to need.
Can anyone suggest anything suitable?
Adam32
- Someone-Else
- Senior Member
- Posts: 14830
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2605 times
What consumer unit?
Post by Someone-Else »
I don't want to rain on your parade, but in the electrical industry, a lot has changed in 12 years.
Just a few points.
1) Moving a consumers unit is a notifiable job, he will also need to issue the correct paper work
2) It will also need Part P paperwork
3) The size of tails has increased, so has the colour of said tails
4) All the current earthing arrangements will need to be checked / upgraded as required
5) RCBO's are quite common
6) No more plastic consumers units
7) SPD's are not unusual (Most fit them as standard)
8) AFDD's exist too.
9) Smart switches and lights are a "thing" now.
10) If it is as bad as you say, it may be better to get it re-wired.
Like I said, I don't want to rain on your parade, but your friend is well out of date, and I am surprised he did not tell you that you can't have 4 electric showers in a house* I can only suggest you get several quotes to have the work done for you safely and with the correct paper work.
*You could, but you would need to have them all interlocked. (Loads of money, and more trouble than its worth, but then its not my money.)
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Senior Member
- Posts: 1366
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
Neelix
-
- Senior Member
- Posts: 1587
- Joined: Fri Aug 01, 2014 8:57 am
- Location: Essex
- Has thanked: 285 times
- Been thanked: 403 times
What consumer unit?
Post by London mike 61 »
When we had our extension built about 7 years ago we had 2 consumer boards fitted and that gives us loads of capacity. We have solar panels and this hasn’t given us any problems .
We have BG consumer boards.
Mike
We have BG consumer boards.
Mike
If it ain't broke, don't fix it!!
London mike 61
Adam32
-
- Senior Member
- Posts: 198
- Joined: Fri Jul 01, 2016 7:30 am
- Has thanked: 12 times
- Been thanked: 5 times
What consumer unit?
The capacity is not an issue. There is zero chance that they would all be used at the same time. There is only 2 of us in the house! I just want to make all rooms en-suit, as we like to change our sleeping room frequently.Someone-Else wrote: ↑Thu Nov 16, 2023 1:25 am your friend is well out of date, and I am surprised he did not tell you that you can't have 4 electric showers in a house*
So any recommendations on consumer units?
Adam32
- Someone-Else
- Senior Member
- Posts: 14830
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2605 times
What consumer unit?
Post by Someone-Else »
Everyone has their own opinion on which consumers unit is best, as you should not be changing it, why not get the person who is changing it to get the one they like.
Yes it is, but its not the capacity of the CU in question.
Obviously you do not have to take my advice, that is your choice, but at the end of the day I want you to be able to come back and ask another question, I don't want to find out you went ahead and DIY then found out someone was electrocuted because of your error, or that your house caught fire because of something you did.
You also need to test everything to make sure it is safe, I know you have a friend who will help you, but IF his meter is still working, one thing is for sure, it will be long out of calibration.
Do the job properly, its cheaper in the long run.
FWIW I am following a post of "Future you" He wants to sell the house, but can't as he does not have the correct paperwork
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Senior Member
- Posts: 1366
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
What consumer unit?
Ask the spark doing the work BUT make sure its a RCBO unit with SPD
Neelix
- ericmark
- Senior Member
- Posts: 4293
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 118 times
- Been thanked: 785 times
What consumer unit?
I would go all RCBO, but as to consumer units, nearly all rated at 100 amp, in theory they can go to 125 amp, but never seen one. Over that they are not consumer units, just distribution units.
I thought with 14 RCBO's I had enough, but when solar was fitted needed a second one. EV charging is complex, with in some cases type B RCD's required and RDC's.
I have once gone down the LABC route, they wanted to see calabration certificates and qualification, I only have 17th edition, over £100 to get 18th so never bothered, have C&G 2391 and a degree in electrical engineering but still had problems getting LABC to accept my signature.
I thought with 14 RCBO's I had enough, but when solar was fitted needed a second one. EV charging is complex, with in some cases type B RCD's required and RDC's.
I have once gone down the LABC route, they wanted to see calabration certificates and qualification, I only have 17th edition, over £100 to get 18th so never bothered, have C&G 2391 and a degree in electrical engineering but still had problems getting LABC to accept my signature.
ericmark
-
- Newly registered Member
- Posts: 24
- Joined: Thu Nov 16, 2023 10:26 am
- Has thanked: 3 times
- Been thanked: 0
What consumer unit?
Post by derek_bartram »
Get your hands on the BS7671 On Site Guide, and take a look at Appendix 1 Maximum Demand and Diversity...
"Water-heaters (instantaneous type), in individual household installations: 100% f.l. of largest appliance + 100% f.l. of second largest appliances + 25% f.l. or remaining appliances"
derek_bartram
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE