Add new outlets in house with original fuse box

All your electrical questions regarding electrics from within the United Kingdom

Moderator: Moderators

Post Reply
cday
Newly registered Member
Posts: 3
Joined: Tue Sep 24, 2024 4:52 pm
Has thanked: 0
Been thanked: 0

Add new outlets in house with original fuse box

Post by cday »

My house was built in 1968 and still has the original fuse box with wired fuses.

I want an electrician to add to the existing ring main a new spur for a combi boiler and a new dual 13A outlet.

Is it correct that in order to comply with the current regs the fuse box will have to be replaced by a modern consumer unit?
yartin
Senior Member
Posts: 1256
Joined: Fri Jun 09, 2017 11:55 am
Has thanked: 144 times
Been thanked: 124 times

Add new outlets in house with original fuse box

Post by yartin »

I am not electrician but I don't think you need to replace on the basis you can still buy fuse wires today from the likes of B&Q, Wickes ....etc.

But I would replace the fuse box to current rcbo or whatever they are called.
Neelix
Senior Member
Posts: 1303
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

Add new outlets in house with original fuse box

Post by Neelix »

If your house and CU date back to the 1960’s then improvements are long overdue.

Yes a new CU with RCBOs and SPD are in order and I would suspect that you may find the main earth is undersized and equipotential bonding missing
cday
Newly registered Member
Posts: 3
Joined: Tue Sep 24, 2024 4:52 pm
Has thanked: 0
Been thanked: 0

Add new outlets in house with original fuse box

Post by cday »

Neelix wrote: Tue Sep 24, 2024 6:31 pm If your house and CU date back to the 1960’s then improvements are long overdue.

Yes a new CU with RCBOs and SPD are in order and I would suspect that you may find the main earth is undersized and equipotential bonding missing
Fine in principle, but installing a consumer unit, which I understand would then require all the house wiring to be tested, would greatly increase the cost of simply adding two new outlets!

The existing system still works, I'm not aware of any campaigns to get householders to upgrade, and my building insurance doesn't ask whether the property has a modern consumer unit.

But my question is whether that extra work is required by the current [English] regs?
OnlyMe
Approved Electrician
Posts: 3114
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Add new outlets in house with original fuse box

Post by OnlyMe »

The additions/alterations require RCD protection. It would be difficult to do with the existing setup.

How do you know that the 1968 installation works? I don't just mean that the sockets work but are they actually earthed?
cday
Newly registered Member
Posts: 3
Joined: Tue Sep 24, 2024 4:52 pm
Has thanked: 0
Been thanked: 0

Add new outlets in house with original fuse box

Post by cday »

OnlyMe wrote: Tue Sep 24, 2024 6:57 pm The additions/alterations require RCD protection. It would be difficult to do with the existing setup.
If that is so, I presume you know, there are inexpensive RCD units that can be installed in the individual circuits?

How do you know that the 1968 installation works? I don't just mean that the sockets work but are they actually earthed?
I am at least pretty sure the existing outlets all have earth connection, I have had some 13A outlets doubled...

More of a concern, perhaps, is that some wiring has the 'green fluid' characteristic of cables from that period, a risk of nuisance trips if the circuits are protected by RCDs or RCBOs, maybe when I am (dream on) away in the winter?

So, ultimately, the house really needs a full rewire, although a spur and new 13A outlet should actually operate satisfactorily for the foreseeable future?
User avatar
Someone-Else
Senior Member
Posts: 14576
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2559 times

Add new outlets in house with original fuse box

Post by Someone-Else »

The "green fluid" is the plasticiser in the cables breaking down the cable. Just because your sockets have an earth connection, doesn't mean they actually have an earth, and if the wiring is that old, it was common then for lighting circuit to be wired in twin cable, NOT twin and earth.

The real "problem" with electricity is that you can't see it, you can't smell it, you can't hear it, but it can kill you in a second, by which time It's too late. Just because something works, does not mean that it is safe. But at the end of the day it's your choice to live in a dangerous place, not mine.

Electricity has no prejudices, it will kill anyone.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Neelix
Senior Member
Posts: 1303
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

Add new outlets in house with original fuse box

Post by Neelix »

Given you have noticed the green goo I would strongly advise you to have an EICR before you do anything
OnlyMe
Approved Electrician
Posts: 3114
Joined: Sun Apr 24, 2011 6:01 pm
Location: South Yorkshire
Has thanked: 225 times
Been thanked: 662 times

Add new outlets in house with original fuse box

Post by OnlyMe »

cday wrote: Tue Sep 24, 2024 9:35 pm
OnlyMe wrote: Tue Sep 24, 2024 6:57 pm The additions/alterations require RCD protection. It would be difficult to do with the existing setup.
If that is so, I presume you know, there are inexpensive RCD units that can be installed in the individual circuits?

How do you know that the 1968 installation works? I don't just mean that the sockets work but are they actually earthed?
I am at least pretty sure the existing outlets all have earth connection, I have had some 13A outlets doubled...

More of a concern, perhaps, is that some wiring has the 'green fluid' characteristic of cables from that period, a risk of nuisance trips if the circuits are protected by RCDs or RCBOs, maybe when I am (dream on) away in the winter?

So, ultimately, the house really needs a full rewire, although a spur and new 13A outlet should actually operate satisfactorily for the foreseeable future?
You are a troll. FOAD.
User avatar
ericmark
Senior Member
Posts: 4260
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 116 times
Been thanked: 782 times

Add new outlets in house with original fuse box

Post by ericmark »

The rules allow surface wiring or wiring using special wires not to be RCD protected, but it would require new RCD sockets, so outlet protected.

The date when all lights other than pendants needed to be earthed was 1966, but also around that time Ian Smith in South Africa caused a copper shortage, and some aluminium cable was used, today aluminium not used with cables under 25 mm² and it caused a lot of problems.

As to plasticiser leaching out, only cure is rewire, and until done don't touch cables, as they can crack as they become brittle as the plasticiser leaches out, you know it needs upgrading, and although I know you don't want the expense, in real terms you don't really have an option.
Neelix
Senior Member
Posts: 1303
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

Add new outlets in house with original fuse box

Post by Neelix »

cday wrote: Tue Sep 24, 2024 6:45 pm
Fine in principle, but installing a consumer unit, which I understand would then require all the house wiring to be tested, would greatly increase the cost of simply adding two new outlets!

The existing system still works, I'm not aware of any campaigns to get householders to upgrade, and my building insurance doesn't ask whether the property has a modern consumer unit.

But my question is whether that extra work is required by the current [English] regs?
Neelix
Senior Member
Posts: 1303
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

Add new outlets in house with original fuse box

Post by Neelix »

Neelix wrote: Thu Sep 26, 2024 5:00 pm
cday wrote: Tue Sep 24, 2024 6:45 pm
Fine in principle, but installing a consumer unit, which I understand would then require all the house wiring to be tested, would greatly increase the cost of simply adding two new outlets!

I'm not aware of any campaigns to get householders to upgrade,
Neelix
Senior Member
Posts: 1303
Joined: Mon May 03, 2021 1:36 pm
Has thanked: 117 times
Been thanked: 212 times

Add new outlets in house with original fuse box

Post by Neelix »

Neelix wrote: Thu Sep 26, 2024 5:00 pm
Neelix wrote: Thu Sep 26, 2024 5:00 pm
cday wrote: Tue Sep 24, 2024 6:45 pm
I'm not aware of any campaigns to get householders to upgrade,
Quite so - the muppets who update the regs do ABSOLUTELY NOTHING to educate Joe Public and its left to the sparks on the front line to educate customers.

Having just retired as a spark it used to drive me MAD having to tell people about this AND as changed can occur every 3 - 4 years its tough on home owners too

AND the regs are so poorly written you can get differing opinions from different sparks
User avatar
ericmark
Senior Member
Posts: 4260
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 116 times
Been thanked: 782 times

Add new outlets in house with original fuse box

Post by ericmark »

Neelix wrote: Thu Sep 26, 2024 5:03 pm AND the regs are so poorly written you can get differing opinions from different sparks
Oh your not kidding. We read the regs and in good faith do some thing, then the regs are clarified, if new not so bad as it always says designed after and a date with every new edition, but when clarified, that means one may have done something which were not permitted, but at the time no one realised.

We need a degree in English to work out what it says some times. And as to remembering what was permitted in 1965, that can also be a problem, filament lamps installed in a room having a non-conducting floor, mounted at such a height that they cannot readily be touched and are out of reach of earthed metal. Could be installed without an earth. However lack of filament lamps today means this rule even in 1965 one would have not have been allowed to wire most lamps without an earth.

This all changed in 1966.

But when some one tries to read it wrong to save them work is different "The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any, other purpose." Note the full stop, it than continued "Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3." Was read by some as if not single core they could over-marked, but any English student would realise that is not the case, but the number of tank thermostats and wall thermostats where the green-and-yellow was over sleeved I have lost count.

So it is really down to who ever is signing the certificate as to what they allow.