Wiring double sockets
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
-
- Newly registered Member
- Posts: 8
- Joined: Mon Sep 25, 2023 10:46 pm
- Has thanked: 6 times
- Been thanked: 0
Wiring double sockets
Post by Malamute01 »
Hi there
Any advice appreciated on this.
I replaced a number of double sockets in a friend's house recently with double sockets that had USB ports. It was pretty straightforward as most of the existing sockets only required a maximum of two wires to be inserted into each of the connectors on the back of the new sockets.
But in one of the rooms there were three feeds as it were (in grey sleeving). One of those contained multi-stranded cable (for the live, neutral and earth wires) and the terminal on the back of the new sockets was nowhere near big enough to accept the multi-strand cable and two other cables into the same terminal.
Is there any way around this other than rewiring the room with modern wiring?
Many thanks.
Any advice appreciated on this.
I replaced a number of double sockets in a friend's house recently with double sockets that had USB ports. It was pretty straightforward as most of the existing sockets only required a maximum of two wires to be inserted into each of the connectors on the back of the new sockets.
But in one of the rooms there were three feeds as it were (in grey sleeving). One of those contained multi-stranded cable (for the live, neutral and earth wires) and the terminal on the back of the new sockets was nowhere near big enough to accept the multi-strand cable and two other cables into the same terminal.
Is there any way around this other than rewiring the room with modern wiring?
Many thanks.
Malamute01
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Wiring double sockets
Post by Someone-Else »
Remove the multi stranded cable. From your description it sounds like it is a small flex.
If there is a fault the circuit protection device (Fuse/mcb/rcbo) should operate. If there is a cable that is too small there is a chance the cable will overheat and start a fire.
It is probably too small in size to be protected by the circuit protection device, so if you don't connect it, there is nothing to be concerned about.
If there is a fault the circuit protection device (Fuse/mcb/rcbo) should operate. If there is a cable that is too small there is a chance the cable will overheat and start a fire.
It is probably too small in size to be protected by the circuit protection device, so if you don't connect it, there is nothing to be concerned about.
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 8
- Joined: Mon Sep 25, 2023 10:46 pm
- Has thanked: 6 times
- Been thanked: 0
Wiring double sockets
Post by Malamute01 »
Thanks for the reply.Someone-Else wrote: ↑Tue Dec 03, 2024 10:24 pm Remove the multi stranded cable. From your description it sounds like it is a small flex.
If there is a fault the circuit protection device (Fuse/mcb/rcbo) should operate. If there is a cable that is too small there is a chance the cable will overheat and start a fire.
It is probably too small in size to be protected by the circuit protection device, so if you don't connect it, there is nothing to be concerned about.
Apologies if I haven't explained that very well. But I'm a little confused . . .
So, basically try wiring up the socket using the two twin and earth cables that DON'T contain the multi-threaded cable and then test it using a socket tester like this?
- Screenshot 2024-12-03 at 23.12.16.png (404.1 KiB) Viewed 623 times
Malamute01
- Someone-Else
- Senior Member
- Posts: 14827
- Joined: Sat Sep 01, 2012 6:03 pm
- Has thanked: 48 times
- Been thanked: 2604 times
Wiring double sockets
Post by Someone-Else »
Tape will come off over time, wagos would be better.
- These users thanked the author Someone-Else for the post:
- Malamute01 (Wed Dec 04, 2024 12:09 am)
- Rating: 7.14%
Above are my opinions Below is my signature.
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.
If gloom had a voice, it would be me.
Click Here for a video how to add/change pictures
Inept people use the QUOTE BUTTON instead of the QUICK REPLY section
Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section

Someone-Else
-
- Newly registered Member
- Posts: 8
- Joined: Mon Sep 25, 2023 10:46 pm
- Has thanked: 6 times
- Been thanked: 0
Wiring double sockets
Post by Malamute01 »
OK, I'll give that a go. I used a couple of Wago connectors on some of the other sockets because the wiring had been cut way too short.
Malamute01
-
- Senior Member
- Posts: 1366
- Joined: Mon May 03, 2021 1:36 pm
- Has thanked: 118 times
- Been thanked: 219 times
Wiring double sockets
Randomly disconnecting cable’s often can have unexpected consequences
- These users thanked the author Neelix for the post:
- Malamute01 (Wed Dec 04, 2024 11:50 am)
- Rating: 7.14%
Neelix
- Argyll
- Senior Member
- Posts: 6201
- Joined: Wed Sep 10, 2008 3:58 pm
- Has thanked: 1191 times
- Been thanked: 583 times
Wiring double sockets
A photo would have been advantageous.
- These users thanked the author Argyll for the post:
- Malamute01 (Wed Dec 04, 2024 11:50 am)
- Rating: 7.14%
Argyll
-
- Newly registered Member
- Posts: 8
- Joined: Mon Sep 25, 2023 10:46 pm
- Has thanked: 6 times
- Been thanked: 0
Wiring double sockets
Post by Malamute01 »
Good point. I'll take some pictures the next time I'm at my friend's house.
Malamute01
-
- Newly registered Member
- Posts: 8
- Joined: Mon Sep 25, 2023 10:46 pm
- Has thanked: 6 times
- Been thanked: 0
Wiring double sockets
Post by Malamute01 »
I'll try to get some pictures the next time I'm at the property which might make the situation clearer . . .
Malamute01
-
- Approved Electrician
- Posts: 3132
- Joined: Sun Apr 24, 2011 6:01 pm
- Location: South Yorkshire
- Has thanked: 225 times
- Been thanked: 664 times
Wiring double sockets
It does not sound like it's a small flex - if it was then there would be no problem fitting it in the socket terminals with the other two cables.Someone-Else wrote: ↑Tue Dec 03, 2024 10:24 pm Remove the multi stranded cable. From your description it sounds like it is a small flex.
If there is a fault the circuit protection device (Fuse/mcb/rcbo) should operate. If there is a cable that is too small there is a chance the cable will overheat and start a fire.
It is probably too small in size to be protected by the circuit protection device, so if you don't connect it, there is nothing to be concerned about.
OnlyMe
-
- Senior Member
- Posts: 686
- Joined: Mon Sep 17, 2012 2:40 pm
- Has thanked: 26 times
- Been thanked: 174 times
Wiring double sockets
If its just a case that the terminal space on the double socket will not accommodate 3 cores into each, would it be worth considering this double socket
MK K2747STWHI 2 Gang 13 Amp Rapid Fix Switched Socket

MK K2747STWHI 2 Gang 13 Amp Rapid Fix Switched Socket

Scotty001
- ericmark
- Senior Member
- Posts: 4293
- Joined: Tue May 10, 2011 2:43 am
- Location: Mid Wales
- Has thanked: 118 times
- Been thanked: 785 times
Wiring double sockets
MK sockets will take two 6 mm sq or three 2.5 mm sq cables, but other makes do seem to have smaller terminals. It is often a problem trying to take a spur from a ring final with small terminals on some makes. More than three wires in a terminal can mean one not clamped well enough, but a spur can only feed one socket or FCU, if using a FCU then that in turn can feed as many sockets as you like, as long as the loop impedance is within limits.
The tester shown does not test loop impedance,
this does, but it is a lot more expensive, working in your own house OK, but in someone else's house, you really should be testing, and complete the minor works certificate, basic to watch ones own back, I know you can cheat and put in figures which seem reasonable, but courts would not really expect anyone to fill in a minor works and not have actually tested, so if in the future something goes wrong, they are likely to believe you if you say it was OK when I tested it before leaving.
The tester shown does not test loop impedance,
- Loop-RCD-tester.jpg (5.81 KiB) Viewed 444 times
ericmark
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE