Earthing on plastic plug sockets
All your electrical questions regarding electrics from within the United Kingdom
Moderator: Moderators
-
- Newly registered Member
- Posts: 33
- Joined: Fri Jan 05, 2007 3:15 pm
- Location: Reading Berkshire
- Has thanked: 0
- Been thanked: 0
Earthing on plastic plug sockets
Post by brayleyboy »
I hope somebody can help.
Over the weekend I have replaced some pretty old plastic plug sockets with some new plastic ones i bought at screwfix. The old double sockets had one terminal each for live/neutral/earth. Each terminal was wired up to the relevant wire from both the circuit cables (i.e. both live cables into live etc.) which is what i expected.
The new sockets still have one live/neutral terminal so I have wired these up in the same way. However the new socket has 2 earth terminals. At present I have just wired up both earth wires to one of the earth terminals, but should the earth from 1 circuit cable be wired up to one terminal, and the the earth from the other circuit cable to the other?
The question I have is, is it essential that I change it, and if so does it matter which earth goes to which terminal? Also there doesnt seem to be an earth cable attached to the metal back box, is this essential?
I have not yet replaced the fuse for the circuit with the sockets in, and would welcome some advice.
Many thanks
Over the weekend I have replaced some pretty old plastic plug sockets with some new plastic ones i bought at screwfix. The old double sockets had one terminal each for live/neutral/earth. Each terminal was wired up to the relevant wire from both the circuit cables (i.e. both live cables into live etc.) which is what i expected.
The new sockets still have one live/neutral terminal so I have wired these up in the same way. However the new socket has 2 earth terminals. At present I have just wired up both earth wires to one of the earth terminals, but should the earth from 1 circuit cable be wired up to one terminal, and the the earth from the other circuit cable to the other?
The question I have is, is it essential that I change it, and if so does it matter which earth goes to which terminal? Also there doesnt seem to be an earth cable attached to the metal back box, is this essential?
I have not yet replaced the fuse for the circuit with the sockets in, and would welcome some advice.
Many thanks
brayleyboy
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Re: Earthing on plastic plug sockets
Post by ultimatehandyman »
You should really put one of the earth wires into each of the earthing terminals as this is how it is shown in the IEE on site guide. You should also really put an earthing wire from the socket to the backbox, this is known as supplementary earthing.brayleyboy wrote:I hope somebody can help.
Over the weekend I have replaced some pretty old plastic plug sockets with some new plastic ones i bought at screwfix. The old double sockets had one terminal each for live/neutral/earth. Each terminal was wired up to the relevant wire from both the circuit cables (i.e. both live cables into live etc.) which is what i expected.
The new sockets still have one live/neutral terminal so I have wired these up in the same way. However the new socket has 2 earth terminals. At present I have just wired up both earth wires to one of the earth terminals, but should the earth from 1 circuit cable be wired up to one terminal, and the the earth from the other circuit cable to the other?
The question I have is, is it essential that I change it, and if so does it matter which earth goes to which terminal? Also there doesnt seem to be an earth cable attached to the metal back box, is this essential?
I have not yet replaced the fuse for the circuit with the sockets in, and would welcome some advice.
Many thanks
You can see how to do this on this page that shows how to change a light switch..- http://www.ultimatehandyman.co.uk/repla ... switch.htm
It's worth doing it the correct way. I have no idea why the earth wires should go into each terminal as most of the sockets I have changed have always been wired to just one terminal. I am sure there is some reason for it.
ultimatehandyman
-
- Newly registered Member
- Posts: 33
- Joined: Fri Jan 05, 2007 3:15 pm
- Location: Reading Berkshire
- Has thanked: 0
- Been thanked: 0
Post by brayleyboy »
Thanks for the quick reply. I will change the way they are wired.
Although I would be interested to know why it makes a difference if anybody knows.
Does it matter which earth I put into which terminal? And which earth terminal I use to supplementary bond to the back box? or both?
Also can I buy earth wire at B&Q/Focus etc and is there a special type for this? Also one of my sockets doesnt have the green/yellow sleaving on the earth wires, where can I get that?
Thanks
Although I would be interested to know why it makes a difference if anybody knows.
Does it matter which earth I put into which terminal? And which earth terminal I use to supplementary bond to the back box? or both?
Also can I buy earth wire at B&Q/Focus etc and is there a special type for this? Also one of my sockets doesnt have the green/yellow sleaving on the earth wires, where can I get that?
Thanks
brayleyboy
skiking
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Sparkydude will know the reason for putting one wire in each terminal, perhaps it is a fail safe incase one drops out, there is always the other one?
It doesn't matter which earth wire goes to which terminal, or which one you put the supplementary earthing wire into.
You should be able to get some earthing wire from B&Q although you will pay through the nose for it. A specialist electrical shop would be better as they will sell you one meter etc. The green and yellow sleeving can be bought at most places and costs pence.
Normally the earthing wire for the supplementery bonding is cut from the cable that is being used to supply the circuit, a piece is cut and then sheathed with green and yellow sleeving. I think for sockets it should be 1.5mm wire.
It doesn't matter which earth wire goes to which terminal, or which one you put the supplementary earthing wire into.
You should be able to get some earthing wire from B&Q although you will pay through the nose for it. A specialist electrical shop would be better as they will sell you one meter etc. The green and yellow sleeving can be bought at most places and costs pence.
Normally the earthing wire for the supplementery bonding is cut from the cable that is being used to supply the circuit, a piece is cut and then sheathed with green and yellow sleeving. I think for sockets it should be 1.5mm wire.
ultimatehandyman
-
- Senior Member
- Posts: 268
- Joined: Wed Feb 28, 2007 12:17 pm
- Location: Newcastle T&W
- Has thanked: 0
- Been thanked: 1 time
uncle buck
-
- Newly registered Member
- Posts: 33
- Joined: Fri Jan 05, 2007 3:15 pm
- Location: Reading Berkshire
- Has thanked: 0
- Been thanked: 0
Post by brayleyboy »
Thanks for all the info
i feel confident doing this work, however can anyone confirm whether I would be breaking any regulations doing it myself?
Also I dont believe the back boxes have specific earthing terminals for supplementary earth, is it ok to use one of the spare fixing brackets (for use with the old style face plates with two screws at the top and two at the bottom)?
Thanks
i feel confident doing this work, however can anyone confirm whether I would be breaking any regulations doing it myself?
Also I dont believe the back boxes have specific earthing terminals for supplementary earth, is it ok to use one of the spare fixing brackets (for use with the old style face plates with two screws at the top and two at the bottom)?
Thanks
brayleyboy
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Like for like replacement of electrical items is allower under the new part p rules, unless they have changed them again
Iv'e never seen any boxes without the earthing terminal, but I can't see a problem attaching the earth wire to where you suggest.

Iv'e never seen any boxes without the earthing terminal, but I can't see a problem attaching the earth wire to where you suggest.
ultimatehandyman
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Post by sparkydude »
theres no reason why both earths should not go ointo one terminal, it is just the way that some manafacturers make their sockets. The MK sockets we use only have one earth terminalin the socket and this is fine. but we do use double sockets with two earth termianls for sockets feeding computer equipment and these circuits have their own high impedance earth ring main so for these circuits you need the two earth terminals as its a bit tight to get two 4mm earths and the two 2.5 earths from the circuit into the one terminal LOL.
As UHM says just make sure you have a supplementary bond from the socket earth termianl to the back box earth terminal if fitted.
Nick
As UHM says just make sure you have a supplementary bond from the socket earth termianl to the back box earth terminal if fitted.
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
sparkydude
-
- Newly registered Member
- Posts: 33
- Joined: Fri Jan 05, 2007 3:15 pm
- Location: Reading Berkshire
- Has thanked: 0
- Been thanked: 0
Post by brayleyboy »
Many thanks for all fo your help everyone. My mind has been put at rest.
I will add the supplementary bonding.
Cheers

I will add the supplementary bonding.
Cheers

brayleyboy
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE