Help with connecting my dimmer switch
Moderator: Moderators
-
- Newly registered Member
- Posts: 3
- Joined: Mon Mar 26, 2007 8:08 am
- Has thanked: 0
- Been thanked: 0
Help with connecting my dimmer switch
Hi there,
I hope someone out there can help me.
I thought I would install a dimmer switch in my daughter's bedroom as I have just finished of decorating it and that would finish it of.
I assumed wiring a dimmer switch would be straight forward even for a novice like me, just follow the wires no problem.
I bought a dimmer switch from homebase and was ready to go.
When I unscrewed the light switch from the wall and seen all the wires I just gave up.
The house is around 30 years old and the electrics are in good condition as I was informed by a spark whom I trust.
This is what is inside the box behind the lightswitch.
Firstly there are 3 grey cables in each of these cables there is a red live and a black neutral wires.There are also the 3 green/yellow wires that that come from the bottom of the box and feed into each of the 3 grey cables.
2 of the red wires are connected to the available screw at the top on the back of the existing light switch and the other is screwed into the bottom of it.
The 3 black wires are capped and do not connect to anything.
I have looked at the back of other light sockets and they are all the same
What I'm not sure of is which of the 3 red wires go into the com and L1 on my dimmer switch ?
I hope my explanation is understood as I lack of electrical description.
Many Thanks
I hope someone out there can help me.
I thought I would install a dimmer switch in my daughter's bedroom as I have just finished of decorating it and that would finish it of.
I assumed wiring a dimmer switch would be straight forward even for a novice like me, just follow the wires no problem.
I bought a dimmer switch from homebase and was ready to go.
When I unscrewed the light switch from the wall and seen all the wires I just gave up.
The house is around 30 years old and the electrics are in good condition as I was informed by a spark whom I trust.
This is what is inside the box behind the lightswitch.
Firstly there are 3 grey cables in each of these cables there is a red live and a black neutral wires.There are also the 3 green/yellow wires that that come from the bottom of the box and feed into each of the 3 grey cables.
2 of the red wires are connected to the available screw at the top on the back of the existing light switch and the other is screwed into the bottom of it.
The 3 black wires are capped and do not connect to anything.
I have looked at the back of other light sockets and they are all the same
What I'm not sure of is which of the 3 red wires go into the com and L1 on my dimmer switch ?
I hope my explanation is understood as I lack of electrical description.
Many Thanks
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
Yes thats fine, all you have is whats known as a loop in system , but instead of using a ceiling rose they run the feeds and the load to the light to the switch box instead of the rose. The three blacks that are capped off in connecter are your neutral in ,neutral out , and neutral to your light fitting, the two reds in the top are live in and live out, and the live on its own is the switched live to your light fitting.
Hope that clarifies your situation
Nick
Hope that clarifies your situation
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
- Rich-Ando
- Pro Tradesman
- Posts: 7138
- Joined: Sat Mar 24, 2007 12:24 pm
- Location: Spondon, Derby
- Has thanked: 135 times
- Been thanked: 304 times
the black wires in a switch are "switched lives" they are not neutrals.
if your house wiring is 30 years old you have the old method of lives being looped to the switches.
without looking ta it i can pretty much say..
all the red cables (live in & two lives out it appears) should connect to C
the black cable connects to L1
if your house wiring is 30 years old you have the old method of lives being looped to the switches.
without looking ta it i can pretty much say..
all the red cables (live in & two lives out it appears) should connect to C
the black cable connects to L1
- sparkydude
- Senior Member
- Posts: 2253
- Joined: Sat Aug 13, 2005 7:11 pm
- Location: Staffordshire
- Has thanked: 2 times
- Been thanked: 149 times
DO NOT DO AS RICH ANDO SAYS
they are not as he says , the blacks ARE NOT SWITCHED LIVES they are NEUTRALS if connected as he has stated then you will get a small explosion and blow your fuse/MCB out.
Nick
they are not as he says , the blacks ARE NOT SWITCHED LIVES they are NEUTRALS if connected as he has stated then you will get a small explosion and blow your fuse/MCB out.
Nick
If it isnt broke dont bloody touch it until it bloody well is and if it is broke then make drawing of the connections before you remove the broken one and replace with a new one LoL
- Rich-Ando
- Pro Tradesman
- Posts: 7138
- Joined: Sat Mar 24, 2007 12:24 pm
- Location: Spondon, Derby
- Has thanked: 135 times
- Been thanked: 304 times
my appologies, i didnt actually read it properly
i saw the usual dimmer switch question and just assumed..
sorry for that, i will make sure i read fully next time.
i saw the usual dimmer switch question and just assumed..
as u know full well, people assume black wires in a switch are neutrals. apart from which, there should never be neutral wires in a switch.This is what is inside the box behind the lightswitch.
Firstly there are 3 grey cables in each of these cables there is a red live and a black neutral wires.There are also the 3 green/yellow wires that that come from the bottom of the box and feed into each of the 3 grey cables.
sorry for that, i will make sure i read fully next time.