Come on lads help solve this one.
Background
New build housse (2 years) - loop system used.
Outside light/ security light (those that switch on when movement is detected) blew a 40w bulb.
Bulb replaced but all other lights downstairs off. Easy, check distribution board for circuit breaker trip - NO trip.
Removed c/b and swopped with upstairs one. Upstairs lights still work. Downstairs with 'new' c/b NOT. So obviously not a faulty c/b.
Check all downstairs light bulbs all fine.
Any suggestions?
Lights Out
Moderator: Moderators
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
- ultimatehandyman
- Site Admin
- Posts: 24425
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Was has happened is that you have had a bad connections and when the circuit blew it disturbed the loose wire meaning tripping all the lights in the circuit out.
Open the consumer unit and check for loose connections to the mcb and neutral of the circuit in question. If none there then if possible, try and follow the cable to the 1st light on that circuit and check that ceiling rose again for loose connections.
More than likely one or the other as you have no lights working at all.
Open the consumer unit and check for loose connections to the mcb and neutral of the circuit in question. If none there then if possible, try and follow the cable to the 1st light on that circuit and check that ceiling rose again for loose connections.
More than likely one or the other as you have no lights working at all.