How many spotlights to replace fluorescent strip light?

Post by MarkJP »

I am currently refitting a kitchen which measures 3.4 x 2.5 metres (11' x 8'6'), which is currently lit by a 1.5 m (5') long fluorescent strip light. The wife wants to dispense with the strip light and install a more stylish looking set of 4 spot lights, but does not want a darker kitchen. How many conventional incandescent light bulbs or halogen or tungsten spot lights would I need to match the fluorescent light output?
Hinton Heating
Gas/Heating Expert
Posts: 4382
Joined: Mon Jan 16, 2006 9:40 pm
Location: Bournemouth
Has thanked: 0
Been thanked: 9 times

Re: How many spotlights to replace fluorescent strip light?

Post by Hinton Heating »

MarkJP wrote:I am currently refitting a kitchen which measures 3.4 x 2.5 metres (11' x 8'6'), which is currently lit by a 1.5 m (5') long fluorescent strip light. The wife wants to dispense with the strip light and install a more stylish looking set of 4 spot lights, but does not want a darker kitchen. How many conventional incandescent light bulbs or halogen or tungsten spot lights would I need to match the fluorescent light output?
It depends upon the brightness of teh spotlights you want to install. What wattage is each one?
User avatar
ultimatehandyman
Site Admin
Posts: 24424
Joined: Sat Jul 16, 2005 7:06 pm
Location: Darwen, Lancashire
Has thanked: 1012 times
Been thanked: 918 times

Post by ultimatehandyman »

Light output is measured in Lumens, if I remember rightly.

A flourescent tends to spread light in all directions whilst spot lights direct the light in one direction. There are lots of factors to consider such as will all 4 spot lights be in a line or will they be a distance apart. Or where you thinking of a rail that has the spot lights on like the picture attached?

For a rough guess I would say 4, but that is just a guess- or get one like the light in the attached picture.
Attachments
meteorwave3-lg.jpg
meteorwave3-lg.jpg (5.58 KiB) Viewed 3432 times
Stoday
Deceased 21-10-2011 R.I.P
Posts: 5945
Joined: Fri Jan 20, 2006 6:03 pm
Location: East of England
Has thanked: 8 times
Been thanked: 90 times

Post by Stoday »

The luminous efficiency of filiament lamps is around 15 lumens per watt, fluorescent 80 Lm/W.

So you need 300 W of lamps in total. So if you have four, each should be 75W. Or six at 50W.

This is only a broad comparison; as pointed out above there are other factors than just the lumen output to consider.
markysparky
Electrician
Posts: 272
Joined: Mon Jan 16, 2006 10:02 pm
Location: Darlington
Has thanked: 0
Been thanked: 0
Contact:

Post by markysparky »

You can now actually get fluorescent recess lights now. They are only 7watt and obviously not as bright as the halogen bullbs.

No info on the net for them. But I did get have a leaflet about them from the wholesalers.......somewhere