Light fitting !!
All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.
Moderator: Moderators
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Light fitting !!
Post by Blueboy4ever »
Hi Guys hope you can help. I have bought a replacement light fitting and cannot get my head around the wiring. On removing my old light there was;
Black and red cable together
Two reds together
Two blacks together
Three yellow/ green together
On the new fitting there is only two wiring points, two marked neutral and two marked live? Please help.
Black and red cable together
Two reds together
Two blacks together
Three yellow/ green together
On the new fitting there is only two wiring points, two marked neutral and two marked live? Please help.
Blueboy4ever
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Hi,
and welcome to the forum.
Is there no earthing point on the light fitting?
What type of light fitting is it? For example is it a fan light etc.
when you say that the wires are together, what exactly do you mean?
Do you mean they were terminated in the same terminal?
and welcome to the forum.
Is there no earthing point on the light fitting?
What type of light fitting is it? For example is it a fan light etc.
when you say that the wires are together, what exactly do you mean?
Do you mean they were terminated in the same terminal?
ultimatehandyman
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Post by markysparky »
The 2 blacks put into the neutrals
the red wire and black wire put into the live
The 2 reds put into a strip connector and that is it. do not connect into the light in any way
Green and yellows go into earth.
the red wire and black wire put into the live
The 2 reds put into a strip connector and that is it. do not connect into the light in any way
Green and yellows go into earth.
markysparky
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Post by markysparky »
I'm assuming that the extra wire for the live is to do another light.
Does the light you are fitting come on with another light by any chance
:
Does the light you are fitting come on with another light by any chance

markysparky
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Blueboy4ever
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Blueboy4ever
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Post by Blueboy4ever »
Have tried what you said MarkySparky, but nothing is happening (no light comes on and the seperate extractor fan is not running).
Blueboy4ever
- ultimatehandyman
- Site Admin
- Posts: 24426
- Joined: Sat Jul 16, 2005 7:06 pm
- Location: Darwen, Lancashire
- Has thanked: 1012 times
- Been thanked: 918 times
Post by ultimatehandyman »
Is there no instruction manual with it?
Are you sure there are no other markings on the fitting besides 2* neutrals and lives?
Is there no symbol that looks like a switch ___/ ___ or similar?
Are you sure there are no other markings on the fitting besides 2* neutrals and lives?
Is there no symbol that looks like a switch ___/ ___ or similar?
ultimatehandyman
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Post by Blueboy4ever »
There are some very brief instructions which state
' If a wiring loop system is used within your home there may be several cables coming out of your ceiling. Before disconnecting your existing light please make a note which cables it is connected to and connect your new fitting to thses wires.'
There are definetly just the four connection points, two Live Terminals and two Neutral terminals.
' If a wiring loop system is used within your home there may be several cables coming out of your ceiling. Before disconnecting your existing light please make a note which cables it is connected to and connect your new fitting to thses wires.'
There are definetly just the four connection points, two Live Terminals and two Neutral terminals.
Blueboy4ever
-
- Senior Member
- Posts: 376
- Joined: Sun Jul 17, 2005 11:38 am
- Location: Newcastle
- Has thanked: 0
- Been thanked: 0
Post by honeymonster »
It sounds like there is a terminal for the permanent live and switched live on the new light, so that the fan can continue to run once the light is switched off.
The instructions seem very poor!
The terminals in the light fitting-
do the two neutrals wire to the same bit inside of the light or are they definately two individual terminals?
The instructions seem very poor!
The terminals in the light fitting-
do the two neutrals wire to the same bit inside of the light or are they definately two individual terminals?
honeymonster
-
- Senior Member
- Posts: 376
- Joined: Sun Jul 17, 2005 11:38 am
- Location: Newcastle
- Has thanked: 0
- Been thanked: 0
honeymonster
-
- Electrician
- Posts: 272
- Joined: Mon Jan 16, 2006 10:02 pm
- Location: Darlington
- Has thanked: 0
- Been thanked: 0
- Contact:
Post by markysparky »
The red and black wire! are they in the same terminal? They are not in seperate terminals by any chance?
If they are seperate put them together into the L terminal and see what happens
If they are seperate put them together into the L terminal and see what happens
markysparky
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Post by Blueboy4ever »
Tried to put the red and black wires in the same terminal - still nothing. I am going to rip my hair out soon :!:
Blueboy4ever
-
- Newly registered Member
- Posts: 7
- Joined: Sat Oct 14, 2006 11:45 am
- Has thanked: 0
- Been thanked: 0
Post by Blueboy4ever »
Sod it, i have just found a direct replacement for the light that i had originally in my bathroom on Screwfix - so i have ordered it! Can't be doing with that other bloody thing any longer ! Its free to a good home if anybody wants it!
Blueboy4ever
-
- Gas/Heating Expert
- Posts: 4382
- Joined: Mon Jan 16, 2006 9:40 pm
- Location: Bournemouth
- Has thanked: 0
- Been thanked: 9 times
Post by Hinton Heating »
generally a light on a loop circuit will have the following connections
earth - all the earths in a terminal block
Neutral - The loop circuit Neutral (normally 2 blacks) + the bulb Neutral + the fan neural
Perm Live - The loop circuit live (normally 2 reds) + supply to switch (normally red) + live to fan
Switch live - return from light (normally black) + the bulb live + the switch live to fan
There are your 3 terminals on your light! 8-)
earth - all the earths in a terminal block
Neutral - The loop circuit Neutral (normally 2 blacks) + the bulb Neutral + the fan neural
Perm Live - The loop circuit live (normally 2 reds) + supply to switch (normally red) + live to fan
Switch live - return from light (normally black) + the bulb live + the switch live to fan
There are your 3 terminals on your light! 8-)
Hinton Heating
Jump to
- Ultimate Handyman DIY forum
- ↳ Welcome to the Ultimate Handyman DIY Forum
- WELCOME
- ↳ WELCOME
- ↳ About the forums
- UltimateHandyman Discounts
- ↳ Ultimatehandyman Discounts
- ULTIMATE HANDYMAN COMPETITIONS
- ↳ UHM Forum competitions
- SHOW CASE- A place to show us your work
- ↳ Show Case Gallery
- ↳ Rogues Gallery
- TOOL FORUM
- ↳ Power Tool Reviews
- ↳ Bosch
- ↳ budget power tools
- ↳ Dewalt
- ↳ Festool
- ↳ Hikoki/Hitachi
- ↳ Makita
- ↳ Metabo
- ↳ Milwaukee
- ↳ Ryobi
- ↳ Tool Talk
- ↳ Bargain Tools
- ↳ Hand tool reviews
- ↳ Power Tool Manuals
- ↳ Bosch
- ↳ Dolmar
- ↳ ELEKTRA BECKUM
- ↳ Hitachi
- ↳ Husqvarna
- ↳ Jonsered
- ↳ Makita
- ↳ Stihl
- Other DIY
- ↳ Computers
- ↳ communications and broadband
- ↳ Gardeners World
- ↳ Money Saving
- ↳ Vehicle maintenance & Repair
- ↳ Energy Saving
- DIY Forum/Home improvement
- ↳ General DIY forum
- ↳ Acrylic Forum
- ↳ DIY Disasters
- ↳ Stoves
- ↳ Building Forum
- ↳ Carpentry/Joinery Forum
- ↳ Kitchen Fitting
- ↳ Damp Proofing and Remedial problems
- ↳ Electric Forum UK
- ↳ Lighting
- ↳ Alarm Manuals
- ↳ Painting & Decorating Forum
- ↳ Plastering Forum
- ↳ Plumbing Forum
- ↳ Central Heating & Boilers
- ↳ Boiler Manuals
- ↳ Alpha
- ↳ Ariston
- ↳ ATAG
- ↳ Atmos
- ↳ Baxi
- ↳ Biasi
- ↳ Broag
- ↳ Chaffoteux
- ↳ Ferroli
- ↳ Glow-worm
- ↳ Halstead
- ↳ Ideal
- ↳ Intergas
- ↳ Keston
- ↳ Myson
- ↳ Potterton
- ↳ Protherm
- ↳ Ravenheat
- ↳ Saunier Duval
- ↳ Sime
- ↳ Thorn
- ↳ Vaillant
- ↳ Viessmann
- ↳ Vokera
- ↳ warmflow
- ↳ Worcester Bosch
- ↳ Shower Manuals
- ↳ Tiling Forum
- ↳ Metalworking Forum
- General
- ↳ The Lounge
- ↳ The games corner
- ↳ The Grumpy corner
- ↳ The Sport corner
- ↳ The Cookery corner
- ↳ The Music Corner
- ↳ BUY - SELL - FREE