Wiring Extractor Fan

Post by Someone-Else »

Jamster wrote: Tue Nov 23, 2021 8:29 pmfitted a new pull chord in the bathroom
So this new pull cord is only supposed to operate the fan?

Jamster wrote: Wed Nov 24, 2021 6:18 pmHope that all makes sense, in a way?
Yes, it does, thanks.

Jamster wrote: Tue Nov 23, 2021 10:30 pm and the pull chord have different colours too.
Now let the "fun" begin

As you can see there is a 3 core and earth at the fan (Black, Brown and White, Normally it would be grey, not white)

At the switch there is:
A twin and earth (Brown and Blue) I am ok with that.
A 3 core and earth (Blue, Red, Yellow) That is the old colours for 3 core and earth.

Which means...............
Someone-Else wrote: Wed Nov 24, 2021 5:41 pmso this will not be an "instant fix"
There has to be a junction somewhere, where they join/change over. You are going to need to find it. Probably in the loft? When you find it, take a picture please.

Please don't quote all of what I typed when you reply. Just answer yes or no. Picture
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

Someone-Else wrote: Wed Nov 24, 2021 7:33 pm

Please don't quote all of what I typed when you reply. Just answer yes or no. Picture

After a lot of searching, think I’ve found two junction boxs linked with this...
The first one has the brown/blue 2core with earth going to the pull chord joining with another brown/blue/black 3core (assume this is the lighting ring). The black in this is still covered so terminates here. I assume all is good here.

The second one has the old colours red/yellow/blue 3core and earth joining with what I assume is the extractor fan wires (brown/grey/black).
As you can see, the brown goes to the switch live red, the black goes to neutral blue and the grey grey wire meets the yellow...which has been left hanging in the pendant...is this the issue? If so, where should that terminate in the pendant?

Thanks
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

Here’s the pics
Attachments
A19B5D42-9BC6-4268-81AF-F97472133FDC.jpeg
A19B5D42-9BC6-4268-81AF-F97472133FDC.jpeg (301.13 KiB) Viewed 1283 times
2160CACD-9B92-4A91-9147-D06AEF7FE567.jpeg
2160CACD-9B92-4A91-9147-D06AEF7FE567.jpeg (328.63 KiB) Viewed 1283 times
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Wiring Extractor Fan

Post by Someone-Else »

Someone-Else wrote: Wed Nov 24, 2021 7:33 pmPlease don't quote all of what I typed when you reply. Just answer yes or no. Picture
So, what did you do?

If you ask a moderator nicely (no, its not me) to correct your error
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

Sorry about that...I don’t use the forums often enough and I got in the habit of clicking the quote button as a reply. My bad. Apologies. Very annoying.

So can you offer any more advice after seeing the pics and having read the description?
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

Any help please?
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Wiring Extractor Fan

Post by Someone-Else »

DO NOT QUOTE ME!

(Late) Lunch time

At the switch what voltage do you get between the two blues (in a choc bloc) and the genuine Brown (NOT the yellow with sleeving, and not the red with sleeving)

Your answer in numbers and or Picture ONLY

DO NOT QUOTE ME!

Quoting all of what was typed makes things hard to follow. (I like an easy life)
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

247v
Attachments
D3FAA3BE-3F74-41C4-A17D-ECEA74CECA5B.jpeg
D3FAA3BE-3F74-41C4-A17D-ECEA74CECA5B.jpeg (255.91 KiB) Viewed 1257 times
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Wiring Extractor Fan

Post by Someone-Else »

DO NOT QUOTE ME!

At the switch:
This will be "interesting" you may have to pull the 3 core and earth down a bit.
Connect the Yellow (with brown sleeving) to the SAME terminal as the Plain brown.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Wiring Extractor Fan

Post by Someone-Else »

DO NOT QUOTE ME!

At the fan:
Connect as follows:
Black to terminal N (Probably still there)
White (I think it may be grey) to terminal L
Brown to terminal LT

Switch mains back on, listen to fan, is it running?
If it is running leave it for 5 minutes, does it stop
If it does not stop, pull the cord ONCE wait five minutes does it stop
If It is not running pull the cord ONCE fan should start
Wait 5 minutes (Fan should still be running)
Pull cord ONCE wait 5 minutes fan should stop.

DO NOT QUOTE ME!
These users thanked the author Someone-Else for the post:
Jamster (Thu Nov 25, 2021 11:04 pm)
Rating: 7.14%
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Jamster
Newly registered Member
Posts: 25
Joined: Fri Feb 14, 2020 10:39 pm
Has thanked: 1 time
Been thanked: 0

Wiring Extractor Fan

Post by Jamster »

That seems to have done the trick.
Fan is on, then stays on for the 2minutes timer after the pull cord is off, so seems all is well and good.
Thanks for your patience, for taking the time out the past couple of evenings and putting up with all the quoting, ha.

Thanks again
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

Wiring Extractor Fan

Post by Someone-Else »

Jamster wrote: Thu Nov 25, 2021 11:09 pmThat seems to have done the trick
I figured it would.

Thanks for letting us know all is well (Don't often get feedback) But also take away from this, that quoting whole replies on ANY forum is bad etiquette it is annoying.
Above are my opinions Below is my signature.