10 wires, 4 holes...

All electrical lighting questions in here please. Including outside lighting and light switch / dimmer questions.

Moderator: Moderators

Post Reply
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Have wired a few basic switches but come across a bit of a mix that I don't know where to begin. Have tried to get in contact with a couple.of electricians to do the job but all fully booked. I'm capable of following instructions (sometimes) so hoping someone can help

I have attached 2 pictures. One of the current 2 gang 2 way wiring
Current
Current
20231208_200446.jpg (192.53 KiB) Viewed 16070 times
and the other of the socket I wish to fit. The black from.the 2 core and outside light blue are joined.
New
New
20231211_205628.jpg (157.84 KiB) Viewed 16070 times
There is a 4 core wire to an outside light on left and 4 core to a 2 way landing light on right. I am unsure of the 2 core routing.

The switch I am fitting has L(A) L1, L2 and B.

Any help would be greatly appreciated

Daniel
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

10 wires, 4 holes...

Post by Someone-Else »

That is a 2 gang 2 way smart switch. It is not compatible with what you have. You would be better off installing a smart lamp.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Someone-Else wrote: Mon Dec 11, 2023 9:19 pm That is a 2 gang 2 way smart switch. It is not compatible with what you have. You would be better off installing a smart lamp.
Could you explain why in layman's terms? It may explain why I couldn't figure it out though. Haha. The switch is sold as a 2 gang 2 way switch.

And thank you
User avatar
Someone-Else
Senior Member
Posts: 14628
Joined: Sat Sep 01, 2012 6:03 pm
Has thanked: 47 times
Been thanked: 2575 times

10 wires, 4 holes...

Post by Someone-Else »

They do not "speak" the same language.
Above are my opinions Below is my signature.

Would you hit a nail with a shoe because you don't have a hammer? of course not, then why work on anything electrical without a means of testing Click Here to buy a "tester" just because it works, does NOT mean it is safe.

:mrgreen: If gloom had a voice, it would be me.

:idea1: Click Here for a video how to add/change pictures


Inept people use the QUOTE BUTTON instead of the QUICK REPLY section :-)
Bob225
Senior Member
Posts: 4764
Joined: Sun Jan 31, 2010 9:21 pm
Location: Kent, Land of Apples and PYO
Has thanked: 100 times
Been thanked: 876 times

10 wires, 4 holes...

Post by Bob225 »

to wire that type of switch you need to have a master switch and a slave switch, you can utilize the existing wiring

https://ilumos.com/pages/2-way-wiring

your current switch is 2 gang - 1 gang is 2 way and the other gang is 1 way

the switch you have purchased is 1 gang 2 way by the looks of it
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Nope, it's definately the 2 gang 2 way I bought. I have the slave switch which is the same without the L2.
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Bob225 wrote: Tue Dec 12, 2023 8:53 pm to wire that type of switch you need to have a master switch and a slave switch, you can utilize the existing wiring

<span class="skimlinks-unlinked">https://ilumos.com/pages/2-way-wiring</span>

your current switch is 2 gang - 1 gang is 2 way and the other gang is 1 way

the switch you have purchased is 1 gang 2 way by the looks of it
I have seen that link but couldn't work out which wires to use fom the diagram
User avatar
ericmark
Senior Member
Posts: 4265
Joined: Tue May 10, 2011 2:43 am
Location: Mid Wales
Has thanked: 117 times
Been thanked: 783 times

10 wires, 4 holes...

Post by ericmark »

Two way wiring with standard switches can use two main methods to wire them, one needs a connector in the back box the other does not, so this
two-way-real.jpg
two-way-real.jpg (32.97 KiB) Viewed 15897 times
is the preferred method, but this
two-way-school-boy-cables.jpg
two-way-school-boy-cables.jpg (28.69 KiB) Viewed 15897 times
will work.

However with electronic switches the first method seems to be used, but the com wire does not carry 230 volt but a signal from the slave switch, so one has to follow the wiring diagram which comes with the electronic switch.

Also counting wires on original it seems you have two gang, and on new either it is only one gang, or it is using wireless connection to the slave, I was surprised not to see a wiring diagram on web site at first. but it did say:-

"Note: I LumoS 2 Way Switches can only work with another I LumoS 2 Way Switch and will not work with Mechanical Switches. I LumoS 2 Way Dimmer switch must be connected to another I LumoS 2 Way Dimmer Switch. A 2 Way Dimmer cannot work with a 2 Way On/Off by design. All I LumoS 2 Way Switches can also be used as an intermediate switch to create a 3 Way and 4 Way system. Please refer to the 2 Way and 3 Way Technical Support page for further assistance with wiring and operation."

On hunting further I did find the wiring diagram and it shows only 2 wires go switch to switch, not three as with mechanical switches.
Bob225
Senior Member
Posts: 4764
Joined: Sun Jan 31, 2010 9:21 pm
Location: Kent, Land of Apples and PYO
Has thanked: 100 times
Been thanked: 876 times

10 wires, 4 holes...

Post by Bob225 »

Do you have a pic of the front of the switch

your current switch

The 2 way circuit is (C) yellow, (L1) blue and (L2) Yellow

The 1 way circuit Is (C) 2x red, (L1) single Red

what wires do you have at the other switch as you have a twin and earth and 2 triple and earth cables
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Thank you all for your help. I have an electrician lined up for in a couple of weeks if I can't figure it out. I don't like giving up though. Haha
Bob225 wrote: Sun Dec 17, 2023 6:13 pm Do you have a pic of the front of the switch

your current switch

The 2 way circuit is (C) yellow, (L1) blue and (L2) Yellow

The 1 way circuit Is (C) 2x red, (L1) single Red

what wires do you have at the other switch as you have a twin and earth and 2 triple and earth cables
The current switch is just a typical 2 switch.

The front of the I lumos is
20231217_195404.jpg
20231217_195404.jpg (178.16 KiB) Viewed 15756 times
The other switch is below. The right hand side is the same light
20231217_195157.jpg
20231217_195157.jpg (182.72 KiB) Viewed 15756 times
Bob225
Senior Member
Posts: 4764
Joined: Sun Jan 31, 2010 9:21 pm
Location: Kent, Land of Apples and PYO
Has thanked: 100 times
Been thanked: 876 times

10 wires, 4 holes...

Post by Bob225 »

It gets even more complex as you have another 2 way circuit

L is your common live, L1 and B is the 2 way

L2 is your 1 way circuit
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

Bob225 wrote: Mon Dec 18, 2023 7:42 pm It gets even more complex as you have another 2 way circuit

L is your common live, L1 and B is the 2 way

L2 is your 1 way circuit
Thank you very much. Really appreciate it
Dan&sarah
Newly registered Member
Posts: 18
Joined: Sat Mar 20, 2021 9:03 am
Has thanked: 5 times
Been thanked: 1 time

10 wires, 4 holes...

Post by Dan&sarah »

All fitted and working well. For anyone having issues in the future these require a light fitting to actually be wired up. They seem to check for load via the electronics in the switch. Took us a while to figure that out.
These users thanked the author Dan&sarah for the post:
Bob225 (Wed Jan 17, 2024 9:38 am)
Rating: 7.14%
Bob225
Senior Member
Posts: 4764
Joined: Sun Jan 31, 2010 9:21 pm
Location: Kent, Land of Apples and PYO
Has thanked: 100 times
Been thanked: 876 times

10 wires, 4 holes...

Post by Bob225 »

The triac/mosfet needs a load to operate as it uses a common live between 3 way, no neutral also makes it more complex
Post Reply